Hello All,
Please I need your help.
I have a LP-steam boiler discharge preesure 10 psig, located 600 feet from a building. The pressure entering the bldg. 5 psig. I allow 5 psig pressure drop for the run, and 5 psig to the bldg. The bldg. area 5312 sq.ft and the total steam load 480 #/hr for 3 UH, 1 HV, I used 1/2 psig/100' pressure drop.
I found the pump capacity:GPM=(480 #/hr)/(20*500)=48
I calculate and found 3" LPS pipe, and 2" CR pipe. How much head I should use if the bldg. roof 24 feet. And how much I should pitch the Supply/Condesate return, is 1/4" per 10' ok.Is these calculations are ok.
Best regards.
Please I need your help.
I have a LP-steam boiler discharge preesure 10 psig, located 600 feet from a building. The pressure entering the bldg. 5 psig. I allow 5 psig pressure drop for the run, and 5 psig to the bldg. The bldg. area 5312 sq.ft and the total steam load 480 #/hr for 3 UH, 1 HV, I used 1/2 psig/100' pressure drop.