Condensate Return/ Pump Capacity/ Head 1

Status
Not open for further replies.

w1999

Mechanical
Jul 20, 2004
7
Hello All,
Please I need your help.

I have a LP-steam boiler discharge preesure 10 psig, located 600 feet from a building. The pressure entering the bldg. 5 psig. I allow 5 psig pressure drop for the run, and 5 psig to the bldg. The bldg. area 5312 sq.ft and the total steam load 480 #/hr for 3 UH, 1 HV, I used 1/2 psig/100' pressure drop.
I found the pump capacity:GPM=(480 #/hr)/(20*500)=48
I calculate and found 3" LPS pipe, and 2" CR pipe. How much head I should use if the bldg. roof 24 feet. And how much I should pitch the Supply/Condesate return, is 1/4" per 10' ok.Is these calculations are ok.
Best regards.
 
Replies continue below

Recommended for you

Even allowing for another 20#/hr for line loss on the steam run, I figure your pressure drop will be less than 1 PSI over the 600 feet of 3". These lines should slope about 1/2" in 10 feet, but the steam line should slope to the building, and the condensate line should slope back to the boiler area. The cond pump will need to handle about 1 GPM (500 #/hr steam will give you 1 USGPM). If the condensate has to discharge into a pressurized tank, like a DA, make sure that you factor this into the discharge head required for the pump.

Remember to allow for expansion on these lines.
 
Hello TBP,

1 GPM all I need, what about delta T.
1 GPM=(500#/hr)/500, (500=8.3lbs/gal*60 min/hr)

GPM=(500#/h)/(20 F*500)= 500*975 BTUH/10000=48.75 GPM

How about the lift, (600'+300')for fitting, elbows*0.04=36 feet.

Best regards.









 
Is there a steam to hot water HX in the building? If there is, then there will be two pumps - one for condensate return, and another one to circulate the water through the building loop.
 
No, there is no hot water HX. The bldg. is 80'x64'.
The total steam load to the bldg. 480 #/hr
for (3)48#/hr UH, (1)18#/hr UH and
(1)314 #/hr for HV unit. The HV unit has
5120 CFM,
face velocity=640 fpm,
Entering DBT=15 F
Leaving DBT=72 F
Steam Temp.=227 F

Thank you for your help.
 
You only need the one pump, and that's for the condensate. The only calc needed for the pump GPM is the steam load in #/hr, divided by 500. Forget the part of the calc that's giving you 48 GPM - that's for a pumped hot water system. Steam will move itself - no pump required.

I can tell that you're not a "steam guy". You should likely find somebody from Spirax Sarco, Armstrong, Bell & Gossett, etc in your area to walk you through this.
 
Thank you TBP for these info.
You the only one who got back to me.
I am still new in Engineering Field, "Steam", etc.

Thank you again.
 