hidalgoe
Electrical
- Jan 14, 2002
- 42
Is it considered good, contemporary design practice to connect a temporary or permanent load to an outside substation critical power panel?
The substation in question has a 12.47kV/4.16YkV,3750kVA transformer with two secondary Cutler-Hammer/Westinghouse
VCP-W vacuum CBs. This substation supplies power to a host of offices and critical 24x7 type facilities at our government installation.
A 4.16kV/120/240V, 25kVA, single phase, transformer provides power to a critical power panel (125A main CB).
This panel supplies control power to reclosing relays (79)and breaker motors and to a battery charger for the vacuum breakers tripping function.
Substation illumination is supplied from this panel also.
(This load was connected to the critical power panel before I arrived).
A contractor is suggesting that a 60A service sourced from the critical panel for an EPA Superfund load simply because it is cheap and convenient (there are no reasonably close power sources). I am proposing that a utility transformer (say 45kVA) be installed at the substation to handle miscellaneous loads such as the one being proposed. The only problem for the contractor is that this will cost more money.
The substation in question has a 12.47kV/4.16YkV,3750kVA transformer with two secondary Cutler-Hammer/Westinghouse
VCP-W vacuum CBs. This substation supplies power to a host of offices and critical 24x7 type facilities at our government installation.
A 4.16kV/120/240V, 25kVA, single phase, transformer provides power to a critical power panel (125A main CB).
This panel supplies control power to reclosing relays (79)and breaker motors and to a battery charger for the vacuum breakers tripping function.
Substation illumination is supplied from this panel also.
(This load was connected to the critical power panel before I arrived).
A contractor is suggesting that a 60A service sourced from the critical panel for an EPA Superfund load simply because it is cheap and convenient (there are no reasonably close power sources). I am proposing that a utility transformer (say 45kVA) be installed at the substation to handle miscellaneous loads such as the one being proposed. The only problem for the contractor is that this will cost more money.