Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Contactor Overload Trip Curves 1

Status
Not open for further replies.

Hawkas

Electrical
Jan 18, 2009
14
Do contactor thermal overloads have the same type of trip curve characteristics as circuit breakers. And if so, how do you specify this, and is this information generally printed on overload labels??
 
Replies continue below

Recommended for you

No. Thermal overload relays are listed as Class 10, Class 15, Class 20 and Class 30. The number relates to the tripping time at 6x setting. Most manufacturers publish the standard curves. I'm not sure which standard defines them - I'll have a look at work when I get there.


----------------------------------
image.php

If we learn from our mistakes I'm getting a great education!
 
In the US, the standard is carried by UL now under UL508 although originally it was NEMA standard ICS-2 (but NEMA is not an approval or testing agency, hence the adoption by UL). For IEC, it is IEC 947-4-1. They are not exactly the same, but close enough not to worry about the differences.


"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln
For the best use of Eng-Tips, please click here -> faq731-376
 
Thanks jraef.


----------------------------------
image.php

If we learn from our mistakes I'm getting a great education!
 
You can use an I^2*T curve wiht the "class" as the tripping time at 600% of rated current. It won't be exact, but it'll be close enough. If you're coordinating closer than the accuracy this statement produces, you're doing it wrong.

old field guy
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor