Summer reheat, winter heating and humidification would also be required in addition to air conditioning. The air conditioning unit must be designed for 50F supply during summer to attain the 40% RH requirement. Summer reheat is required to not overcool the space with the 50F supply air required for dehumidification. Winter humidification is required when outdoor air dewpoint is less than 36F. Refer to pyschrometric chart.