Cooling tower in winter - slow down fan speed 1

Status
Not open for further replies.

spacebeer

Mechanical
Oct 24, 2016
13
Hi,

I need some help here with some calculations.
I have the following cooling tower:
Thermal power: 1997 kW
Water flowrate: 26,5 l/s
Water inlet temp. (process): 48,5 ºC
Water outlet temp. (process): 30,5 ºC
Dry bulb temp.: 37,0 ºC
Wet bulb temp.: 24,0 ºC
Air flowrate: 40,1 m3/s

So i can obtain from the psychrometric chart the outlet conditions of the air in this situation.

But, if i have the following conditions in the winter:
Dry bulb temp.: 8,0 ºC
Wet bulb temp.: 6,3 ºC
Is it possible to slow down the fan speed ??
 
Replies continue below

Recommended for you

Tower fan speed control based on sump temperature as a first step of control as well as a tower bypass system should do the job for you in winter
 
Ok thanks!
But i'm trying to preview how much can i save in this winter conditions.
So, for this i want to know the air flowrate in this situation. That's my problem....

Thanks
 
Youir energy savings will depend upon DB and coincident WB temperatures in winter
 
SAK9 has the answer about a bypass system for winter operations. Such bypass system for example is used by ice skating rinks in my region.
 