Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Tek-Tips community for having the most helpful posts in the forums last week. Way to Go!

Countersunk Holes and Implied 90 3

Status
Not open for further replies.

engAlright

Mechanical
Jun 12, 2003
240
0
0
CA
Section 1.8.12 of Y14.5-2009 indicates that for countersunk holes "...the diameter and included angle of the countersink are specified.".

In the corresponding figure 1-39 the countersink feature is shown dimensioned with a 90° angle.

Why is an angle dimension required when the included angle is 90°? Would an implied 90° angle (section 1.4i) not apply? This is the only instance I can think of where a 90° angle needs to be shown on the drawing.

Thanks!
 
Replies continue below

Recommended for you

Well seems like I'm in the minority...consensus seems to be that showing the angle is the way to go. It still seems weird to show a 90° angle dimension on a drawing but I understand that the tendency will be to assume the Engineer has forgotten to add a dimension, rather than assuming an implied 90 applies.

And for reference ANSI metric countersink angles are 90°.
 
Status
Not open for further replies.
Back
Top