We are currently approached to comment on cracks found on slab-on-grade and would like to ask for your idea on its causes and prevention. Cracks are found on corners especially near the stiffer retaining wall ( 250mm thk others are 150mm thk only )and also at the center of the slab. Building dimension is around 70m x 70m

History :
1.) Sub-grade has passed FDT tests done per layer of
300mm. FDT is at least 96%.

2.) Slab is resting on a loose gravel base ( 100mm thk )
with polythelene vapor barrier just below the slab
on top of the gravel base coarse.

3.) The Slab thickness is 200mm ( 8 inches ) doubly
reinforced ( two layers )with 16mm dia spaced
500mm OC.

4.) Concrete cover is 25mm ( 1 inch )thus saw-cutted
contraction joints are limited to 25mm deep.

5.) Contraction joint is at around 7.0m x 9.0m.

6.) slab reinforcements are anchored to the perimeter
retaining walls.

Initially, we have identified as probable causes the following items:

1.) The contraction joint is too shallow thus not able
to give enough weak plane for the crack to follow
once it shrinks. Usual depth is at 1/4 the depth

2.) The slab is fully restrained by the retaining wall
thus creating the cracks.

3.) Contraction joints are spaced farther than usual
( usual is sround 16 to 24 feet for an 8-in slab)

We are also looking as a probable reason the Loose gravel base ( no binders ) under the Slab but could not find an article on this matter.

Measures to prevent farther cracks from occuring we are looking into :

1.) Deepening the saw cut
2.) Deep saw cutting the perimeter to free up the slab

Kindly give your comments.

Best regards and more knowledge!!!








 
Replies continue below

Recommended for you

The timing of sawing is widely considered to be far more important than depth of sawing. Sawing should be performed as soon as practicable. More sawing now more may be ineffectual in preventing additional cracking. If you wanted to epoxy inject the existing cracks and make deeper, more closely spaced contraction joints, well that's a whole different story.


Techmaximus
 
That's a lot of steel in an 8" slab.
What type of operation occurs on the floor?
How long has the slab been in service?
 
With that thick of a slab, and if the slab is "restained" at its perimeter, what you have is a huge mass of concrete generating a lot of heat of hydration during curing, and a large amount of shrinkage as the concrete hardens over a period of a about 2 months. Could be the cause - shrinkage cracking.
 
If your reinforcing continues through your contraction/control joints, then the joints probably are ineffective. I would have used about 30% more steel in the slab to prevent shrinkage cracks, based on the formula that appears on page 21 of the PCA publication "Concrete FLoors on Ground (2nd Ed.). You'll see about half the final shrinkage after about 12 months.

If you can live with them, just leave them alone. Whenever I've seen repairs to cracks, the repair has only highlighted them and made them really ugly.
 
I agree with techmaximus on the timing...it is critical.

jmiec also correctly points out that the quantity of steel is likely making your sawcut joints less effective.

The list of variables causing cracking is quite long. We do need more info to help solve this, such as:

How long after placement were the joints cut?
What was the slump of the concrete at placement?
How well was the grade of the gravel controlled?
When did the cracks first appear?
What are the shape, size, and depth of the cracks?
Have you done a crack map on the surface of the concrete?
Is there any faulting of the cracks?
What were the weather conditions at time of placement and for the first 36 or so hours afterward?
Was there a curing procedure and for how long?

Most likely your cracks are related to drying shrinkage, though you could have some plastic shrinkage influence as well. The cracks near the wall are likely from the wall restraint condition.
 
Thank you for your responses.

For the inquiries :

The slab is quite new, just over a month.

It will be used for some processing of products watches and its components also for conveying raw materials on a racking system. The reinforcing bars was adapted all throughout the slab in case big loads will be used. ( Reinforcing bars : 16mm dia @ 500mm OC, two layers ).

Could the uncompacted gravel base coarse without binders ( fine sand ) have any effect on the cracking?
 
The gravel base can have an effect if it is uneven or was displaced during placement. That's one of the problems with using a gravel base...I don't usually allow it unless there is a need for capillary barrier. I prefer a clean, compacted, fine sand subbase.
 
If you're seeing cracks after one month, then disregard my previous post, as the cracks are probably not due to drying shrinkage. Concrete at one month is only beginning to shrink.

In addition to Ron's excellent set of questions, is it possible that the perimeter walls settled?
 
A vapor barrier directly below the slab creates an unequal drying condition for the slab.

As the slab hydrates, the bleed water will go in all directions, including up to the surface and down to the bottom of the slab. The water at the surface will tend to evaporate unless the slab is cured correctly, ie., kept moist and at a good temperature (above 50 degreesF F). If the rate of evapoartion is faster than the rate of bleeding, the top of the slab will dry out. However, the bottom of the slab is still quite moist because the vapor barrier retains the bleed water. This unequal drying creates significant stresses and usually is the main reason for curling in a slab.

In the case of a floating slab, the slab will curl up, therefore it woll not be support by the sub-base, and any load will inevitably crack the slab. (this load will usually occurs when the Contractor grinds the slab to get rid of the curling.) When the slab is tied into the foundation, the reinforcing at the edges restrains the slab and the crack will form at the nearest point of least resistance.

SOLUTION = Either place vapor barrier directly below slab and CURE CORRECTLY, or place vapor barrier below 6-8" of pourous sub-base and to allow bleed water at bottom to move away and then CURE CORRECTLY.

Hope this helps.
 
VIPE, I follow the posts in this forum in effort to learn more about engineering. Especially concrete, my niche. I am familiar with curling as a result of thermal expansion/contraction and the friction induced between a slab and grade. I find the reversal of tensile and compressive stesses with respect to deflected member shape interesting. I am also familiar with thermal bow induced by temperature variant within the member itself. I am curious to learn more about curling as a result of different curing rates. For my benefit, is there a reference you point me to so that I can learn more about this type of stress.
 
Blake989,
You can check out ACI 302.1R "Guide for Concrete Floor and Slab Construction" see section 9.2. ACI 212.4R, section 5.7, last paragraph, ACI 224R,"Control of Cracking in Concrete Structures" section 3.4.4.

Hope this helps.
 
At least some of these cracks sound like they can be attributed to drying shrinkage. The solution to avoid them in the future would be to use Type K, shrinkage-compensating cement, because it expands rather than shrinks.
 