ksdphilippines
Structural
- Jun 20, 2002
- 36
We are currently approached to comment on cracks found on slab-on-grade and would like to ask for your idea on its causes and prevention. Cracks are found on corners especially near the stiffer retaining wall ( 250mm thk others are 150mm thk only )and also at the center of the slab. Building dimension is around 70m x 70m
History :
1.) Sub-grade has passed FDT tests done per layer of
300mm. FDT is at least 96%.
2.) Slab is resting on a loose gravel base ( 100mm thk )
with polythelene vapor barrier just below the slab
on top of the gravel base coarse.
3.) The Slab thickness is 200mm ( 8 inches ) doubly
reinforced ( two layers )with 16mm dia spaced
500mm OC.
4.) Concrete cover is 25mm ( 1 inch )thus saw-cutted
contraction joints are limited to 25mm deep.
5.) Contraction joint is at around 7.0m x 9.0m.
6.) slab reinforcements are anchored to the perimeter
retaining walls.
Initially, we have identified as probable causes the following items:
1.) The contraction joint is too shallow thus not able
to give enough weak plane for the crack to follow
once it shrinks. Usual depth is at 1/4 the depth
2.) The slab is fully restrained by the retaining wall
thus creating the cracks.
3.) Contraction joints are spaced farther than usual
( usual is sround 16 to 24 feet for an 8-in slab)
We are also looking as a probable reason the Loose gravel base ( no binders ) under the Slab but could not find an article on this matter.
Measures to prevent farther cracks from occuring we are looking into :
1.) Deepening the saw cut
2.) Deep saw cutting the perimeter to free up the slab
Kindly give your comments.
Best regards and more knowledge!!!
History :
1.) Sub-grade has passed FDT tests done per layer of
300mm. FDT is at least 96%.
2.) Slab is resting on a loose gravel base ( 100mm thk )
with polythelene vapor barrier just below the slab
on top of the gravel base coarse.
3.) The Slab thickness is 200mm ( 8 inches ) doubly
reinforced ( two layers )with 16mm dia spaced
500mm OC.
4.) Concrete cover is 25mm ( 1 inch )thus saw-cutted
contraction joints are limited to 25mm deep.
5.) Contraction joint is at around 7.0m x 9.0m.
6.) slab reinforcements are anchored to the perimeter
retaining walls.
Initially, we have identified as probable causes the following items:
1.) The contraction joint is too shallow thus not able
to give enough weak plane for the crack to follow
once it shrinks. Usual depth is at 1/4 the depth
2.) The slab is fully restrained by the retaining wall
thus creating the cracks.
3.) Contraction joints are spaced farther than usual
( usual is sround 16 to 24 feet for an 8-in slab)
We are also looking as a probable reason the Loose gravel base ( no binders ) under the Slab but could not find an article on this matter.
Measures to prevent farther cracks from occuring we are looking into :
1.) Deepening the saw cut
2.) Deep saw cutting the perimeter to free up the slab
Kindly give your comments.
Best regards and more knowledge!!!