I'm preparing to wire up a WEG small 110V 1.5 HP single phase capacitor start motor, and need to pick up some Male & Female insulated spade connectors. I chose to use these as space in the motor end cavity is very limited. The wires in the motor are 14 Ga. stranded copper. The AC line in comes from a standard orange 16/3 extension cord. There are 2 other wires (red & black) that appear to be 18 Ga.
The wiring diagram shows making two 3-wire connections. What size crimp connector do I need to get 3 wires twisted into it?
Also, I don't see direction of rotation indicated on the motor. What do I change if I need it to be reversed? This is just driving a large 40" drum fan with a V-belt. Motor turns 3450 rpm with a 2" pulley to a 9" pulley on the fan shaft. Big airflow!
Your thoughts?
 
 https://files.engineering.com/getfile.aspx?folder=7879f9d5-0d9b-4169-bc97-88f86a11b42c&file=20200724_162538.jpg
Replies continue below

Recommended for you

First, change out the 16/3 for a 12/3.
# 16 AWG is less than 1/2 of the cross sectional area that you need.
Second, more than one wire in a spade connector is a code and approvals violation and poor work practice.

[link ]Bill[/url]
--------------------
"Why not the best?"
Jimmy Carter
 
Also, at 110V the motor draws >17A, you will need a 20A dedicated circuit for it, it will NOT be able to be plugged into a standard 15A receptacle circuit. The limit for a standard 15A circuit is about 3/4HP


" We are all here on earth to help others; what on earth the others are here for I don't know." -- W. H. Auden
 
you will need a 20A dedicated circuit for it
And that 20 Amp dedicated circuit may be protected by a 40 Amp breaker.
And if the fan and motor are permanently mounted, the extension cord is unacceptable.
It may be time to hire a professional.

[link ]Bill[/url]
--------------------
"Why not the best?"
Jimmy Carter
 
The fan is not permanently mounted. It is placed where cooling is needed. What is correct connection for all the wiring inside the motor cavity? Within such a limited space, room for connecting hardware is at a premium. It's really gonna be stuffed in tight. Add to that the diameter of 12/3 upgrade. According to the wiring label, I don't see how you can avoid having multi-wire connections.
 
Try ring lugs and small bolts.
Under Canadian rules a 1.5 HP motor needs a suitable motor controller.
What say the NEC?
You probably need a 30 Amp receptacle and plug.
It should not be interchangeable with the plug for your electric clothes drier.

[link ]Bill[/url]
--------------------
"Why not the best?"
Jimmy Carter
 
gkitf16's

Agreed with the above comments. To reverse rotation switch T5 and T8.

Best Regards

Petronila
 