Hello everyone! I have a crosstie with 180 degree hook at both ends, is it allowed based on ACI? all i know it stated on the ACI like this one :
25.3.5 Crossties shall be in accordance with (a) through (e):
(a) Crosstie shall be continuous between ends
(b) There shall be a seismic hook at one end
(c) There shall be a standard hook at other end with
minimum bend of 90 degrees
(d) Hooks shall engage peripheral longitudinal bars
(e) 90-degree hooks of two successive crossties engaging
the same longitudinal bars shall be alternated end for end,
unless crossties satisfy 18.6.4.3 or 25.7.1.6.1