Hello everyone! I have a crosstie with 180 degree hook at both ends, is it allowed based on ACI? all i know it stated on the ACI like this one :
25.3.5 Crossties shall be in accordance with (a) through (e):
(a) Crosstie shall be continuous between ends
(b) There shall be a seismic hook at one end
(c) There shall be a standard hook at other end with
minimum bend of 90 degrees
(d) Hooks shall engage peripheral longitudinal bars
(e) 90-degree hooks of two successive crossties engaging
the same longitudinal bars shall be alternated end for end,
unless crossties satisfy 18.6.4.3 or 25.7.1.6.1
Thankyou!
25.3.5 Crossties shall be in accordance with (a) through (e):
(a) Crosstie shall be continuous between ends
(b) There shall be a seismic hook at one end
(c) There shall be a standard hook at other end with
minimum bend of 90 degrees
(d) Hooks shall engage peripheral longitudinal bars
(e) 90-degree hooks of two successive crossties engaging
the same longitudinal bars shall be alternated end for end,
unless crossties satisfy 18.6.4.3 or 25.7.1.6.1
Thankyou!