CRSI skip joist tables min stirrups 1

Status
Not open for further replies.

haynewp

Structural
Dec 13, 2000
2,327
In CRSI (I have the 2008 version), there is no mention of providing minimum stirrups where Vu is greater than phi*Vc/2 in the Chapter 8 joist tables. The example on page 8-9 also does not mention providing stirrups and only compares the shear to phi*Vc. Does anyone know where this is permitted in ACI 318 for wide module joists? I am getting a shear failure in SpSlab that appears to work by the CRSI tables because SpSlab is using 1/2*phi*Vc as the permitted limit without having any stirrups. The joists in the tables I am looking at do not require the joist tapered ends.
 
Replies continue below

Recommended for you

See this article from which the blurb below was taken.

I believe that this was a change to ACI somewhere along the way. Shear design is allowed to be a bit more liberal when proportions are such that behavior is thought to be that of a ribbed slab rather than an isolated beam. Nowadays, wide module of joists now fall into the category of beams. T-beams to be exact.

c01_pxnfyp.png
 
This is what 318-19 has to say about this issue. There, the transition happens at a joist spacing of 30in.

c01_h9sfmy.png
 