- Feb 18, 2005
- 19,114
Remember the Hydrualic Press...
The 2HP cushion pump is still giving me fits. Today I went back and ran the cushion measuring everything.
A-B 492.5V
B-C 493V
C-A 494V
The electronic overload was tripping in about a minute.
Current:
A 1.4A
B 1.2A
C 1.8A
This represents a nasty 33% mismatch.
I rolled the three phases.
Current:
A 1.2A
B 1.5A
C 1.3A
20% mismatch
I rolled the three phases again.
Current:
A 1.5A
B 1.3A
C 1.15A
24% mismatch
I went back to the first roll. It ran for 15 minutes and tripped.
This is a 2.8A motor barely loaded.
I checked the voltage drop from in front of the fuses to the three motor leads leaving the panel. They all had a 1.0V drop. Fuse contact, fuse, fuse contact, contactor, into terminal block, out of terminal block. (1.0V across the board)
In all cases the high current motor lead remained the high current leg.
I think I am down to the motor and the motor connections. I was told the motor's nine leads were hooked up correctly and all the wire-nuts(groan) were tight. I told them lets try re-terminating the motor connections with compression connectors. If that doesn't improve things we need to yank the motor.
Do you guys concur?
If this motor is taken to a motor shop, (it is still under warranty being about 2 months old and never having run for long), can a typical motor shop check for current balance?
Keith Cress
Flamin Systems, Inc.-
The 2HP cushion pump is still giving me fits. Today I went back and ran the cushion measuring everything.
A-B 492.5V
B-C 493V
C-A 494V
The electronic overload was tripping in about a minute.
Current:
A 1.4A
B 1.2A
C 1.8A
This represents a nasty 33% mismatch.
I rolled the three phases.
Current:
A 1.2A
B 1.5A
C 1.3A
20% mismatch
I rolled the three phases again.
Current:
A 1.5A
B 1.3A
C 1.15A
24% mismatch
I went back to the first roll. It ran for 15 minutes and tripped.
This is a 2.8A motor barely loaded.
I checked the voltage drop from in front of the fuses to the three motor leads leaving the panel. They all had a 1.0V drop. Fuse contact, fuse, fuse contact, contactor, into terminal block, out of terminal block. (1.0V across the board)
In all cases the high current motor lead remained the high current leg.
I think I am down to the motor and the motor connections. I was told the motor's nine leads were hooked up correctly and all the wire-nuts(groan) were tight. I told them lets try re-terminating the motor connections with compression connectors. If that doesn't improve things we need to yank the motor.
Do you guys concur?
If this motor is taken to a motor shop, (it is still under warranty being about 2 months old and never having run for long), can a typical motor shop check for current balance?
Keith Cress
Flamin Systems, Inc.-