This is in relation with a feasibility study I am conducting with regards to options of mitigating high transformer in-rush currents.
I have a downstream 3 phase transformer, delta-wye, with 36A primary at 208VAC with an in-rush currents of Ia=220Arms, Ib=310Arms and 310Arms. This transformer is supplied from a 480-208/120V Delta-wye transformer
Based from the above values, the highest in-rush per phase is at approximately 12x transformer primary FLA. I wish to limit the in-rush to 175.29A per phase. I checked an ABB swtichgear handbook for sizing a current limiting reactor and considered the rated reactor current Ir = 26A,
through kVA of the reactor as SD= 1.732*26*120=5.4038kVA
kVA to be limited, SK"1 = (310A*208)/1.732 = 37.2275kVA
Desired kVA, SK"2 = (175.29A*208)/1.732 = 21.0503kVA
Therefore, the required percentage voltage drop of the reactor (Vr) = (1.1*100%*SD)* [(SK"1-SK"2)/(SK"1*SK"2)]
With this I am getting Vr = 12.271% or 13%
With this Vr=13%, the current is limited to 170.8A
The Voltage Drop at the reactor is also given by:
Ur = (%Vr * Vl-n)/ (1.732*100%)
= (0.13*120)/(1.732) = 9.0VAC
The voltage variation of the system with the insertion of this reactor will also be checked by calculation.
I wish to consult the experts on reactors or anybody who used this ABB switchgear handbook formula if I am in the proper way of applying the formula.
Secondly, are current limiting reactors also effective in mitigating asymmetrical transformer in-rush currents?
Thank you.
I have a downstream 3 phase transformer, delta-wye, with 36A primary at 208VAC with an in-rush currents of Ia=220Arms, Ib=310Arms and 310Arms. This transformer is supplied from a 480-208/120V Delta-wye transformer
Based from the above values, the highest in-rush per phase is at approximately 12x transformer primary FLA. I wish to limit the in-rush to 175.29A per phase. I checked an ABB swtichgear handbook for sizing a current limiting reactor and considered the rated reactor current Ir = 26A,
through kVA of the reactor as SD= 1.732*26*120=5.4038kVA
kVA to be limited, SK"1 = (310A*208)/1.732 = 37.2275kVA
Desired kVA, SK"2 = (175.29A*208)/1.732 = 21.0503kVA
Therefore, the required percentage voltage drop of the reactor (Vr) = (1.1*100%*SD)* [(SK"1-SK"2)/(SK"1*SK"2)]
With this I am getting Vr = 12.271% or 13%
With this Vr=13%, the current is limited to 170.8A
The Voltage Drop at the reactor is also given by:
Ur = (%Vr * Vl-n)/ (1.732*100%)
= (0.13*120)/(1.732) = 9.0VAC
The voltage variation of the system with the insertion of this reactor will also be checked by calculation.
I wish to consult the experts on reactors or anybody who used this ABB switchgear handbook formula if I am in the proper way of applying the formula.
Secondly, are current limiting reactors also effective in mitigating asymmetrical transformer in-rush currents?
Thank you.