D-AVR and PSS testing and tuning interval at Power plant

Status
Not open for further replies.

olicg

Electrical
Aug 3, 2005
31
Is there any standard for performing testing and tuning of a power plant generator AVR/PSS? Or are there any practices around by any utility company.

Thanks,
Olic
 
Replies continue below

Recommended for you

Yes there definitely is - your plant should have the manual that came with the equipment that explains the tuning and other maintenance that is required. If you no longer have the documentation, let me know... I may be able to track it down for you.

Steamguy2
- Discussion & resources for professionals in the Power Generation Industry
 
Hi

What type of test do you mean?

These equipments usually set up and tuned by the manufacturers or planning dept. The performance of the controller can be tested using software and performing stability study.

Tuning of PSS parameters usually have done using the linearized power system with various objective functions or control theories.


 
I am not sure what area you are located in, but I've found useful information at WECC.biz. (WECC = Western Electricity Coordinating Council) The WECC is in charge of coordinating the North American Western Interconnection.

You should be testing your PSS everytime you test your AVR. If you have changed your AVR response you should be re-tuning your PSS. Check the WECC website under Documentation for a basic guide on tuning a PSS.

 
Thanks for all the replies.

I have bought the standard IEEE Std 421.2-1990, IEEE Guide for Identification, Testing,and Evaluation of the Dynamic Performance of Excitation Control Systems.

But even this standard does not mention about periodic testing of AVR which is already in service.

Maybe somebody working in power plant can tell me what practice his/her company is following regarding testing of AVR reponse and tuning.

 