We've had some failures of control circuits of dahlander motors. I believe it was as result of someone fiddling with delay off timer to ensure high speed to low speed does not occur unless motor has first come to standstill.
I'd like to find an authoritative write up of this issue, textbook or link to website/literature that anyone is aware of? Or if someone has the time to develop a good discussion of the problem.
Maybe I'm not using correct search terms but i'm googled out!
apart from finding hits to other eng-tips threads on problems with these motors (which has been valuable) the best i could find was this
From other links i'm aware motor runs as generator and negative slip.
is it a case that a more robust motor (if specified) could tolerate this under worse case conditions, i got that impression reading the eaton stuff.
In our case We are seeing failure of terminations on bottom of high speed contactor (happened on two separate fan starters) and in another case terminations of motor terminal box.
Not discounting poor installing and joints, as it is fairly new system, but the fact that there is rumour of timer being changed at some point makes me think this could be reason. No record of timer setting to compound matters but Ive told them to check the run down time from high speed mode.
I'd like to find an authoritative write up of this issue, textbook or link to website/literature that anyone is aware of? Or if someone has the time to develop a good discussion of the problem.
Maybe I'm not using correct search terms but i'm googled out!
apart from finding hits to other eng-tips threads on problems with these motors (which has been valuable) the best i could find was this
From other links i'm aware motor runs as generator and negative slip.
is it a case that a more robust motor (if specified) could tolerate this under worse case conditions, i got that impression reading the eaton stuff.
In our case We are seeing failure of terminations on bottom of high speed contactor (happened on two separate fan starters) and in another case terminations of motor terminal box.
Not discounting poor installing and joints, as it is fairly new system, but the fact that there is rumour of timer being changed at some point makes me think this could be reason. No record of timer setting to compound matters but Ive told them to check the run down time from high speed mode.