mongo1
Electrical
- Apr 8, 2008
- 5
I recently replaced an old 200HP Louis Allis/Magnatek DC Drive with a new 200HP Baldor BC19H series Drive. After installation and a successfull startup I noticed the F2, F3 & A1 Leads were all terminated together at the motor with the A1 armature lead from the drive (F1 & F4 tied to Drives F+ & F-). assuming this was incorrect I had the F2 & F3 leads isolated from the A1 lead, in doing so the baldor reported a phase loss fault and would not run the motor. I had the F2 & F3 reterminated with the A1 lead and the motors been running fine since and apparently ran like this for years. has anybody ever seen this befor or know what i'm dealing with?