Henrique Orlandini
- Dec 11, 2017
- 19
I'm working in the instrumentation department, and we need to set the alarm and trip point of a centrifugal pump. I'm having trouble with the high pressure trip value.
According to our pump's curve, the highest discharge pressure would be at shut-off head (348 m) with +5% of tolerance, totalizing 365.4 m. That in bar would be about 35.84 bar, and adding the maximum suction pressure (1.5 bar) would give about 37.34 bar, so we set the high pressure trip at 37 bar, while setting the high pressure alarm at 34 bar using the mininum stable flow of the pump.
Our customer commented that this was the worst case scenario, with maximum suction pressure and maximum shutoff head value. He asked what should happen with the alarm and trip if the pump worked outside those conditions, let's say suction pressure of 1 bar and a shutoff head of 348 +3% (which is inside the tolerance). With my calculations, that would leave the pump with a discharge pressure of 36.16 bar, enough to set the high pressure alarm, but not enough to trip it, leaving it running at shutoff.
I thought of using the lowest possible values of suction pressure and shutoff head tolerance, but that would reduce the working range of the pump, causing it to trip at unnecessary moments.
What could be a good solution? Measure the flow at discharge and trip it if goes at a low level (before 0 m³/s) or measure the delta of pressure between discharge and suction and trip it when this delte becomes too high (although I can't see this working).
Could you help me with this? If you need more info, I would be glad to post if I'm allowed to.