rtpnd
Structural
- Jan 19, 2007
- 9
I have a 40' steel beam which requires two splices in it, one about 10' in from each end, where the bending stresses are relatively low vs capacity at the middle of the beam. I'm designing a moment splice connection with steel top and bottom splice plates which will be field-bolted to the flanges with slip-critical bolts (as well as a field-bolted web plate to handle the shear.) I have a couple of questions:
Will the beam deflect significantly more (than in a full-length non-spliced beam) due to the presence of the splices? Is the deflection greater if the splice connection is designed for the full bending capacity of the beam vs. if it is designed for the required moment of the beam at the splice location?
The connection will be substantially more expensive if it has to be for the full moment capacity of the beam, but I suppose I can justify it if it reduces deflection.
How do you go about checking this?
Thanks,
-Ryan
Will the beam deflect significantly more (than in a full-length non-spliced beam) due to the presence of the splices? Is the deflection greater if the splice connection is designed for the full bending capacity of the beam vs. if it is designed for the required moment of the beam at the splice location?
The connection will be substantially more expensive if it has to be for the full moment capacity of the beam, but I suppose I can justify it if it reduces deflection.
How do you go about checking this?
Thanks,
-Ryan