AndersE
Chemical
- Sep 19, 2007
- 18
Hi all,
I am currently working on a FEED phase study for a large, offshore gas production plant. The current design includes three closed loop cooling and heating medium systems, briefly described below:
- Main cooling medium system, normal operating temperatures 34 to 55 °C
- Turbine inlet air cooling medium system, normal operating temperatures 4 to 16 °C
- Heating medium system, normal operating temperatures 140 to 177 °C (pressurized water, not steam)
An amine based acid gas removal system will also be included, which requires continuous high quality demineralized water make-up with the following specifications:
- Max oxygen content: 10 ppmw (ppm by weight)
- Max chloride content: 2 ppmw
- Max calcium (Ca2+) content: 50 ppmw
The current design is based on using this demineralized water as make-up and first fill of the closed loop heating medium and cooling medium systems described above, even though this is not strictly required. The reason for this is that generating two different qualities of water adds more complexity and increases cost.
All closed loop systems are based on carbon steel piping and equipment, and are fitted with nitrogen blanketed expansion tanks. Our current design includes for the batch dosing of corrosion inhibitor, scale inhibitor, pH controller and oxygen scavenger (exact number of chemicals still to be decided) into those closed loop systems, in order to minimize corrosion. The turbine inlet air cooling medium system includes glycol (MEG) for antifreeze protection, while the other systems use only water (except for the corrosion prevention chemicals).
However, one of the engineers from our client is arguing that no chemicals should be needed unless we can calculate the yearly corrosion rate and prove that this is needed. The design plant life time is 30 years. I have been trying to explain that to my knowledge, there are no models that can accurately predict the corrosion rate and that all designs I have seen for other projects add corrosion inhibitor and other chemicals to their closed loop cooling and heating medium systems, but with litte success so far.
The oxygen content of the make-up demineralized water is low, and so is the chloride concentration. But in the closed loop systems, oxygen may enter during maintenance of equipment when flages are opened. Chlorides could potentially enter into the cooling medium system in case of a pin-hole leak in one of the seawater plate heat exchangers. Therefore I am still arguing that it is too risky to design without the provision for corrosion prevention chemicals and that if serious corrosion occurred it could have huge economical consequences. So my question is:
- Is there any reliable and accepted method for calculating the corrosion rate in these systems?
- Would it be possible to achieve a 30 year life time without adding corrosion prevention chemicals?
I am currently working on a FEED phase study for a large, offshore gas production plant. The current design includes three closed loop cooling and heating medium systems, briefly described below:
- Main cooling medium system, normal operating temperatures 34 to 55 °C
- Turbine inlet air cooling medium system, normal operating temperatures 4 to 16 °C
- Heating medium system, normal operating temperatures 140 to 177 °C (pressurized water, not steam)
An amine based acid gas removal system will also be included, which requires continuous high quality demineralized water make-up with the following specifications:
- Max oxygen content: 10 ppmw (ppm by weight)
- Max chloride content: 2 ppmw
- Max calcium (Ca2+) content: 50 ppmw
The current design is based on using this demineralized water as make-up and first fill of the closed loop heating medium and cooling medium systems described above, even though this is not strictly required. The reason for this is that generating two different qualities of water adds more complexity and increases cost.
All closed loop systems are based on carbon steel piping and equipment, and are fitted with nitrogen blanketed expansion tanks. Our current design includes for the batch dosing of corrosion inhibitor, scale inhibitor, pH controller and oxygen scavenger (exact number of chemicals still to be decided) into those closed loop systems, in order to minimize corrosion. The turbine inlet air cooling medium system includes glycol (MEG) for antifreeze protection, while the other systems use only water (except for the corrosion prevention chemicals).
However, one of the engineers from our client is arguing that no chemicals should be needed unless we can calculate the yearly corrosion rate and prove that this is needed. The design plant life time is 30 years. I have been trying to explain that to my knowledge, there are no models that can accurately predict the corrosion rate and that all designs I have seen for other projects add corrosion inhibitor and other chemicals to their closed loop cooling and heating medium systems, but with litte success so far.
The oxygen content of the make-up demineralized water is low, and so is the chloride concentration. But in the closed loop systems, oxygen may enter during maintenance of equipment when flages are opened. Chlorides could potentially enter into the cooling medium system in case of a pin-hole leak in one of the seawater plate heat exchangers. Therefore I am still arguing that it is too risky to design without the provision for corrosion prevention chemicals and that if serious corrosion occurred it could have huge economical consequences. So my question is:
- Is there any reliable and accepted method for calculating the corrosion rate in these systems?
- Would it be possible to achieve a 30 year life time without adding corrosion prevention chemicals?