Determination of critical compressive stress without K value?
StructureMan44
201
I am attempting to determine the critical stress, Fcr, without using the effective length factor, K. If I read this correctly; section C-E3 of AISC 360-10 states that the limit between elastic and inelastic buckling can be defined as F¬e=0.44*Fy. If this is true than Fe depends on Fy (and vice versa) which then means that (Fy/Fe)=2.25 and Fcr is then forced to be equal to equation E3-2. Where is the mistake in this thinking?
I'm going to assume that we're talking about the direct analysis method based on some of your recent posting. In that case, the critical stress should be based on KL = 1.0L.
The fact that the limit between elastic and inelastic buckling occurs at Fe=0.44*Fy does not mean that Fe=0.44*Fy. Fe=pi^2*E/(KL/r)^2, same as always. As KootK mentions, for DAM, K=1.0.
Thanks guys. This wasn't related to the DAM, I was checked the critical stress for a HSS column and was wondering if it's possible to avoid calculating K.
Not without some sort of p-delta or deflection based moment magnification or something. Anything you do to avoid assuming or calculating K is going to be significantly more calculation intensive.
TLHS, don't forget about the reduced stiffness.