Marvie
Electrical
- Dec 15, 2004
- 14
Anyone out there who knows of a site that intensively covers the area of oil dielectric dissipation factor (tan delta)?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
That's not exactly extensive but I assume it is addressing the area of your question: power factor testing of the oil itself.Oil Power Factor. Power factor indicates the dielectric loss (leakage current associated with watts loss) of the oil. This test can be performed by DGA laboratories. It may also be done by Doble testing in the field. A high power factor indicates deterioration and/or contamination from byproducts such as water, carbon, or other conducting particles, including metal soaps caused by acids attacking transformer metals, and products of oxidation. DGA labs normally test oil power factor at 25 EC and 100 EC. Information in Doble Engineering Company Reference Book on Insulating Liquids and Gases RBIL-391, 1993 [10] indicates the in-service limit for power factor is less than 0.5% at 25 EC. If the power factor is greater than 0.5% and less than 1.0%, further investigation is required; the oil may require replacement or Fuller’s earth filtering. If the power factor is greater than 1.0% at 25 EC, the oil may cause failure of the transformer; replacement or reclaiming of the oil is required immediately. Above 2%, oil should be removed from service and replaced because equipment failure is imminent. The oil cannot be reclaimed.