I posted this awhile back, but have still not come up with answer ( that makes sense). Huge generator on newly built nursing home placed at fence line 10 feet away, diesel fuel pipe above that 10 feet from property line, and 13 feet from front porch.
IMC. 501.3.1 requires 30 feet from property line for flammable, fumes, or dusts. 501.3.2 Requires 10 feet for other product conveying outlets.
In the 501.3.1 ICC commentary, they include hazardous exhaust systems as 30 feet distance to reduce exposure to vapors, fumes. This is a huge difference.
Has anyone encountered this problem? Also, the commentary advised code officials to consider prevailing winds in locating hazardous exhausts.
These were the point I made to the Deputy Building Official with no response other than to allow this monster at 10 feet. The wind blows westerly right across into my yard and building. This is a small apartment house. Any advice? Code help on this, I want this thing moved and certainly the exhaust pipe.
IMC. 501.3.1 requires 30 feet from property line for flammable, fumes, or dusts. 501.3.2 Requires 10 feet for other product conveying outlets.
In the 501.3.1 ICC commentary, they include hazardous exhaust systems as 30 feet distance to reduce exposure to vapors, fumes. This is a huge difference.
Has anyone encountered this problem? Also, the commentary advised code officials to consider prevailing winds in locating hazardous exhausts.
These were the point I made to the Deputy Building Official with no response other than to allow this monster at 10 feet. The wind blows westerly right across into my yard and building. This is a small apartment house. Any advice? Code help on this, I want this thing moved and certainly the exhaust pipe.