Recently, on our 12.5 MVA, 15.5 / 6.9 KV Dyn1 transformer, differential relay operated while changing the taps.
The transformer has 17 taps position i.e., +8, .., 0, ..., -8 with a regulation of 10 % voltage.
The incident happened when the operator was changing the tap from -7 to -8 position which is the last one. During TTR, we found out that in a recent maintenance job on OLTC, the drive mechanism was not correctly aligned with the tap position. -7 at local indicator was hooked upto to -8 inside.
The Alstom KBCH120 relay showed 874 A on HV side where a 600/5 CT was used. Load was around 10 % on the transformer. while on LV side it showed 274 A on 1200/5 CT. This mismatch is huge. Esp when we checked the transformer; megger results were excellent, TTR showed one posistion mismatch only, REF relay showed no fault current.
BLS550 is the type of OLTC. Can sb explain what might have happened inside the transformer?
Thanks in advance.
The transformer has 17 taps position i.e., +8, .., 0, ..., -8 with a regulation of 10 % voltage.
The incident happened when the operator was changing the tap from -7 to -8 position which is the last one. During TTR, we found out that in a recent maintenance job on OLTC, the drive mechanism was not correctly aligned with the tap position. -7 at local indicator was hooked upto to -8 inside.
The Alstom KBCH120 relay showed 874 A on HV side where a 600/5 CT was used. Load was around 10 % on the transformer. while on LV side it showed 274 A on 1200/5 CT. This mismatch is huge. Esp when we checked the transformer; megger results were excellent, TTR showed one posistion mismatch only, REF relay showed no fault current.
BLS550 is the type of OLTC. Can sb explain what might have happened inside the transformer?