DTR2011
Electrical
- Oct 12, 2006
- 682
We’re currently commissioning a large substation with A and B systems from different manufacturers. The P&C design has done away with control switches, Lock out relays and replaced with virtual lockouts.
We’ve discovered that on the B system, the non volatile latches, used as 86 devices, are reprogramming themselves to be not used. Contact with the manufacturer has revealed that the problem is repeatable.
This is the first time I’ve experienced anything quite like this. The manufacturer has not offered anything else to try other than to up/down grade firmware, but that hasn’t solved anything and requires a full retest. Due to the complex logic involved, replacing control switches and LORs it takes hours to retest.
The B system was deemed Good Enough to use in the design but that may change shortly.
We’ve discovered that on the B system, the non volatile latches, used as 86 devices, are reprogramming themselves to be not used. Contact with the manufacturer has revealed that the problem is repeatable.
This is the first time I’ve experienced anything quite like this. The manufacturer has not offered anything else to try other than to up/down grade firmware, but that hasn’t solved anything and requires a full retest. Due to the complex logic involved, replacing control switches and LORs it takes hours to retest.
The B system was deemed Good Enough to use in the design but that may change shortly.