Well I just pulled a couple degrees of fanheat off of the top of my head, but it is not unrealistic at all to be higher if it was just a supply fan and there was no return fan.
You mention down stream filters, I hate them but could be some half loaded HEPAs if it is any kind of clean space environment.
But besides air flow, it is just easier for the coil to take the blower heat out directly. More heat going into the coil, more heat it can grab.
If that space load is all sensible, then you end up being forced to dehumidify in order to get the supply air cold enough to compensate for the draw through reheat.
I did a main telephone switch and I took a lot of steps to avoid condensation, including deliberately winding up the air flow so that the supply dry bulb was 5 degrees above the space dewpoint. In my project, blow through was less airflow and less total cooling.
A real humid load and the fan reheat helps you out, but it is at least worth looking at blow through on the big sensible SPACE loads, like SHR>=0.90
Take the "V" out of HVAC and you are left with a HAC(k) job.