stevenal
Electrical
- Aug 20, 2001
- 3,789
This is related to my other question. I was incorrect on the voltage, neighbor has 24.9 kV, ours is 12.47. Both are grounded wye systems feeding unbalanced loads. The 60 degree phase shift can be accommodated with a Yy6 connection by choosing the proper bushings. The transformer size is 3000 kVA. Due to the size, I understand I need a delta tertiary. Do you agree? I understand the tertiary helps reduce tank heating and balances the loading somewhat, but have never seen guidelines based on capacity. Thanks.