JBinCA,
Thanks for your support. I am glad to answer your questions as best I can.
*****1. Why would the manufacturer be a good reference for a "factory" test, but not a "field" test?
Good question. I would say most manufacturers recommend a partial discharge test in the field if the economics warrant it, however, some people on this forum continue to refer to specific manufacturer who has outdated recommendation material on their website.
*****2. Economics factor into testing decisions just as much as they do application / purchasing decisions. XFMRs, gens, motors, SWGR, BKRs, etc are all subjected to more stringent tests in the factory than they regularly are for field acceptance. Why would cable not follow suit?
You are correct. Factory tests are typically more stringent and sometime not achievable in the field. However, where technically possible and economically feasible, I think the industry should strive toward the goal of comparing apples with apples. I don't think anyone can argue with this goal. An example of what you are talking about is the ICEA/AEIC requirement for a factory MV cable insulation test. ICEA recommends an approximate stress in Volts/mil of insulation which equates to about 4Uo. This is impractical in the field so, a good trade off is somewhere between 2 and 3Uo. One would not expect to have transients on a cable system greater than 3Uo so this is a fairly conservative tradeoff.
StineIng,
*****Are there any guidelines for what level of pC are acceptable for cables, joints or other accessories?
Good question. Yes IEEE 400 recommend used the factory levels for the field. So… here you go.
IEEE 400-2001 General Guide Shielded Power Cable Testing
IEEE 48-1996 Terminations No PD ? 5pC at ? 1.5Uo
IEEE 404-2000 Joints No PD ? 3pC at ? 1.5Uo
IEEE 386-1995 Separable Connectors No PD ? 3pC at ? 1.3Uo
ANSI/ICEA S 97-682-2004–HV/EHV Extruded Cable No PD ? 5pC at ? 2.0Uo
ICEA S-93-639-2000 MV Extruded Cable No PD ? 5pC at ? 4.0Uo
IEEE 400.3-2007 Guide to Partial Discharge Testing General description of PD test
*****What method is most used for PD testing ?
OWTS, AC 50-60Hz resonans test, or others??
I assume by ‘test method’ you really mean what voltage source is used the most. Factories almost always use a 50 or 60 Hz series resonant voltage sources. Series resonant voltage sources are also widely used in the field. Most of the statistically significant PD data which has been presented is derived from 50/60Hz work. However, where the use of a series resonant voltage source is not practical for PD tests, very low frequency AC and variable frequency resonant voltage sources are used. Pulsed/ oscillating wave voltage sources are used less frequently. One of the problems with changing the frequency too much from 50/60 Hz is that PD activity behaves differently at different frequencies, at which point, we can no longer compare directly to the standards listed above.
*****Aren't there any startup tests before you charge the cable to 2xUo or more?
Typically the voltage is ramped up to operating voltage first to make sure that that nothing active at or below operation before proceeding to higher voltages.
*****The IEC 62067 recommends you do a DC oversheat and an AC insulation test. Is that recommendation only for HV and not MV.. can't remember..
In my opinion IEC 620607 (Power cables with extruded insulation and their accessories for rated voltages above 150 kV up to 500 kV) is a very lame standard which at the end basically says… “Do what and this standard will cover you.”
Section 14 Guidance for “Electrical tests after installation”:
“For installations where only the oversheath test according to 14.1 is carried out, quality assurance procedures during installation of accessories may, by agreement between the purchaser and contractor, replace the insulation test.
The a.c. test voltage to be applied shall be subject to agreement between the purchaser and the contractor. The waveform shall be substantially sinusoidal and the frequency shall be between 20 Hz and 300 Hz. The voltage shall be applied for 1 h, either with a voltage according to table 10 or with 1,7Uo , depending on practical operational conditions.
Alternatively, a voltage of Uo may be applied for 24h.”
Therefore, you have 3 options. None of which can give you an assurance of reliable future performance.
1) do nothing except inspection during construction
2) perform a 24-hour withstand at Uo (soak test)
3) perform a test for 1 hour at 1.7Uo (hipot test)
In my opinion IEC is far behind IEEE in these matters.
Benjamin Lanz
Vice Chair of IEEE 400
Sr. Application Engineer
IMCORP- Power Cable Reliability Consultants