This question is for a 1-story building, akin to a residential structure.
We have a concrete wall (used for bearing and shear) which changed sizes between the time the footings were poured and when the final documents were released. For the purposes of this question, assume it went from a 14" wall with rebar on both faces to a 10" wall with rebar on both faces. The alignment of one face is maintained, so the other face simply moves in by 4".
The building is located in Seismic Design Category D, which makes us subject to chapter 21 of the 2011 ACI 318. Section 21.12.2.1 stipulates the following:
21.12.2.1 — Longitudinal reinforcement of columns and
structural walls resisting forces induced by earthquake
effects shall extend into the footing, mat, or pile cap, and
shall be fully developed for tension at the interface.
This indicates to us that if we wish to add a new row of reinforcement at the face of the wall that shifted, it would need to be fully developed in the footing. For the dowels that were cast-in, we provided a standard hook. We are using #4's but even at this size of bar, I do not believe we can achieve full development for tension in a 12" footing with 3" of clear cover.
Any ideas on how to detail this transition?
Any ideas on code exceptions that would allow us to develop rebar only for the strength required, rather than for full strength?
I appreciate any help you all can provide.
We have a concrete wall (used for bearing and shear) which changed sizes between the time the footings were poured and when the final documents were released. For the purposes of this question, assume it went from a 14" wall with rebar on both faces to a 10" wall with rebar on both faces. The alignment of one face is maintained, so the other face simply moves in by 4".
The building is located in Seismic Design Category D, which makes us subject to chapter 21 of the 2011 ACI 318. Section 21.12.2.1 stipulates the following:
21.12.2.1 — Longitudinal reinforcement of columns and
structural walls resisting forces induced by earthquake
effects shall extend into the footing, mat, or pile cap, and
shall be fully developed for tension at the interface.
This indicates to us that if we wish to add a new row of reinforcement at the face of the wall that shifted, it would need to be fully developed in the footing. For the dowels that were cast-in, we provided a standard hook. We are using #4's but even at this size of bar, I do not believe we can achieve full development for tension in a 12" footing with 3" of clear cover.
Any ideas on how to detail this transition?
Any ideas on code exceptions that would allow us to develop rebar only for the strength required, rather than for full strength?
I appreciate any help you all can provide.