To protect a centrifugal pump from running dry, a liquiphant (sensor that detects dryness) was installed in the suction side of the pump after the suction strainer (See drawing). If the liquiphant detects dryness, the pump shuts down. The pump sucks water/oil from a vessel and pumps it to a tank. The suction line is positioned approx. 20 cm below the suction nozzle of the pump. To check the function, the suction slide valve was closed. However, the pump continued to run because the liquiphant did not seem to detect dryness. Unfortunately, I cannot explain this. Is it possible that the suction line is not being sucked dry when the suction slide valve is closed and the pump is running? The liquiphant or sensor is located at the top of the pipe and protrudes about 1 cm into the pipe.
Thank you in advance,
Regards Nick
To protect a centrifugal pump from running dry, a liquiphant (sensor that detects dryness) was installed in the suction side of the pump after the suction strainer (See drawing). If the liquiphant detects dryness, the pump shuts down. The pump sucks water/oil from a vessel and pumps it to a tank. The suction line is positioned approx. 20 cm below the suction nozzle of the pump. To check the function, the suction slide valve was closed. However, the pump continued to run because the liquiphant did not seem to detect dryness. Unfortunately, I cannot explain this. Is it possible that the suction line is not being sucked dry when the suction slide valve is closed and the pump is running? The liquiphant or sensor is located at the top of the pipe and protrudes about 1 cm into the pipe.