Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Earth Leakages on Medium Voltage cable 1

Status
Not open for further replies.

David Adeola

Electrical
Oct 1, 2024
1


OUTGOING 11 KV EARTH cable has 65v leakage current what could have been the causes if all the R.M.U were checked and confirmed to be okay.



 
Replies continue below

Recommended for you

@ Mr David Adeola (Electrical)(OP)1 Oct 24 21:35
' OUTGOING 11 KV EARTH cable has 65v leakage current what could have been the causes if all the R.M.U were checked and confirmed to be okay'.
1. Sorry, I have difficulty to understand your question. Perhaps you would like to explain a) what is " outgoing 11 KV EARTH cable,
b) 65v leakage current,
c) R.M.U
2. You are welcome to come back with more detail.
Che Kuan Yau (Singapore)
 
@ Mr Hoxton123 (Electrical)2 Oct 24 16:35
' RMU = Ring Main Unit'
Thank you for your learned advice.
Can you kindly enlighten the relevance of RMU and what are the other items; 11KV EARTH cable and 65v leakage current.
Che Kuan Yau (Singapore)
 
I can only guess 65 V on open delta at secondary of voltage transformers ..
 
It could be the potential difference between the meter earth and the earth point for MV earth cable.

R Raghunath
 
I agree with Raghunat.
In my opinion also, the cable shields of three phases insulated cores was open-not earthed-at one end but earthed at the other end, and the 65V was measured between one shield and the Earth. In this case a capacitive voltage divider was created and the 65V was the part beyond the insulation. That means the core insulation is not damaged.



 
Status
Not open for further replies.

Part and Inventory Search

Sponsor