Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Tek-Tips community for having the most helpful posts in the forums last week. Way to Go!

Earthing grid.

Status
Not open for further replies.

SauravWest

Electrical
Dec 4, 2019
35
0
0
NP
Dear sirs,

When is the right time to start putting earthing mat in substation? The control room building is near to plinth level and foundation of transformer is completed.

Faithfully,
Saurav
 
Replies continue below

Recommended for you

First, a foundation grounding has to be prepared before concrete pouring and to provide connection points for grounding grid.
If the outside equipment and buildings lay-out is final the designed grounding grid [electrodes, horizontal laid copper wire grid and other underground parts of the grounding system] may be installed.
If the "final" lay-out needs to be modified, the eliminated part must be recovered in another area and the new touch and step voltage must be calculated and completed.
 
Also need to consider whether it is a new site or with existing grid elsewhere adjacent.
More control required if interfacing with existing earth grid.
 
Status
Not open for further replies.
Back
Top