BillyBob2021
Electrical
- Sep 28, 2021
- 7
Hello,
We have a pole top recloser with an Eaton from 6 control loop scheme. It lost AC due to an outage and the DC battery back up failed the battery ended up being dead. Now the Loop scheme disabled light is on and the Loop scheme reset light is on. We changed out the battery and checked voltages and all is well. We pushed the LS reset button but nothing happened. Does anyone know how to get the LS enabled again?
Thanks for any help!
Update: we were able to have this reset via SCADA. I’m still confused as to why we couldn’t reset using the reset button but SCADA could reset it.
We have a pole top recloser with an Eaton from 6 control loop scheme. It lost AC due to an outage and the DC battery back up failed the battery ended up being dead. Now the Loop scheme disabled light is on and the Loop scheme reset light is on. We changed out the battery and checked voltages and all is well. We pushed the LS reset button but nothing happened. Does anyone know how to get the LS enabled again?
Thanks for any help!
Update: we were able to have this reset via SCADA. I’m still confused as to why we couldn’t reset using the reset button but SCADA could reset it.