Im dealing with a wall on a slab (balcony) - see attached picture.
What do you guys recommend for an effective width(beff) when designing a slab?

balc_rqjrx9.png
 
Replies continue below

Recommended for you

There probably is some definitive guidance somewhere, but since you asked what we would do, I would use about a metre.
 
Tnx for answer, but Im not dealing with concentrated load.

I dont think I can consider alfa as 45 degrees?
 
Is it a concrete or a masonry wall?

Recommendation von patswfc looks reasonable, I would use it, or go with some FEM program.

Tnx for answer, but Im not dealing with concentrated load.
Well change your line load in x point loads (your program does it too...:)
 
tnx for reply. Its a masonry wall.
 
AASHTO used to have an effective width for cantilever slabs with wheel loads: E=3.75+0.8X, where X is the perpendicular distance from the supporting element to the load. You could treat your wall as a series of concentrated loads and add the effects. You could find out how that formula was derived, or, would drop the 3.75 from the formula and just use E=0.8X.
 