Elevator manufacturer A has indicated that their elevator controllers have an SCCR of 5,000A, with no options for a higher SCCR.

Elevator manufacturer B has indicated that their elevator controllers have an SCCR of 10,000A, with greater SCCRs (14,000A at 600V, 25,000A at 480V, and 45,000A at 208V) attainable with upstream fusing.

Both manufacturers have left me a little confused. First of all, why would a manufacturer be unable to provide controllers with SCCRs above 5,000A? Second, it is my understanding that, with a UL508 control panel, you cannot legally attain a higher SCCR by depending on upstream fusing. (Is my understanding of this correct?)

What is going on here?
 
Replies continue below

Recommended for you

You can't just slap fuses in and say its now a higher rating. The panel can have a rating plate that says it has a certain fault level when protected by a class of fuse with a maximum value.
 
jmbelectrical (Electrical)(OP)4 Nov 23 21:51
" #1. Elevator manufacturer A has indicated that their elevator controllers have an SCCR of 5,000A, with no options for a higher SCCR."
It is my personal opinion that A is very low quality manufacturer with SCCR 5kA, and
with no option for a higher. Avoid the offer even with a lower price.
" #2. Elevator manufacturer B has indicated that their elevator controllers have an SCCR of 10,000A, with greater SCCRs (14,000A at 600V, 25,000A at 480V, and 45,000A at 208V) attainable with upstream fusing".
This is the norm. Manufacturer B is well informed.
" #3. Both manufacturers have left me a little confused. First of all, why would a manufacturer be unable to provide controllers with SCCRs above 5,000A?"
See advice by Mr. sunnysky reference Schneider publication.
" #4. Second, it is my understanding that, with a UL508 control panel, you cannot legally attain a higher SCCR by depending on upstream fusing. (Is my understanding of this correct?)"
Yes. There is NO way you can claim the SCCR complied with UL 508 unless it is tested. The test would state the type of OCPD shall be used up to certain SCCR. You can NOT put in any fuse type/fuse rating or breaker type/breaker rating and claim compliance without expensive tests.
Che Kuan Yau (Singapore)
 
jmbelectrical said:
First of all, why would a manufacturer be unable to provide controllers with SCCRs above 5,000A?
Unable? There is no reason. It is "unwilling". The 5kA is a "courtesy" rating that UL allows for people who put zero effort into it. I can get a 5kA SCCR on a bathtub if I want to. Attaining a higher SCCR is simply a matter of selecting components that have been tested and listed TOGETHER by the manufacturer at higher levels. Virtually every major manufacturer of electrical power components has a table of parts that state what can be used in series with what else and what the attainable SCCR level will be, it is NOT that difficult. The thing is, if I have a Siemens contactor and Siemens Overload, it might be series listed at a higher SCCR with a SIEMENS circuit breaker, but not with a SCHNEIDER circuit breaker. The Series Listing process for the component manufacturer is an expensive destructive test, so why would Siemens test with someone else' circuit breaker? So that panel builder has elected to forego even that simple process of opening up a spreadsheet and possibly changing what brand of contactor or overload relay they use, rather than just shopping for the CHEAPEST thing they can get. It's an indication that they care more about saving a dollar on their component cost than they do about making it possible for an end user to actually install something legally.

Second, it is my understanding that, with a UL508 control panel, you cannot legally attain a higher SCCR by depending on upstream fusing. (Is my understanding of this correct?)
Sort of. End users cannot themselves ATTAIN a higher level on their own in the field, that's true. But the panel manufacturer can, again, get a Series Listing of their panel with fuses, because MOST (if not all) power components will be already be series listed by the manufacturers with specific fuse classes and/or types. So as long as you use them in your panel (in accordance with the aforementioned component series listing table), you are good to go. Alternatively the panel manufacturer can LIST those fuse details in an installation manual and place the burden on the end user to provide those fuses, but in that case it generally must have very SPECIFIC fuse data, such as manufacturers and exact part numbers of compatible products.

Again, getting a higher SCCR is not rocket surgery... it just takes slightly more than doing absolutely nothing! So in my opinion, suppliers who choose to do nothing are the ones to avoid. Better yet, talk to YOUR procurement people about ADDING the requirement for a reasonable SCCR to your tender specifications. That way the lazy vendors don't even bother to bid.