I am currently designing an elevator and machine room for subway. Electrical specification say as below
MAXIMUM ALLOWABLE VOLTAGE VARIATION IS +/- 10% KONE CALC THE FOLLOWING FOR THIS ELEVATOR DUTY
NAME PLATE AMPS : 15
Max ACCEL AMPS : 26
PROTECTION DEVICE REQUIRED PRIOR TO INSTALLATION MAX MOTOR BRANCH SHORT-CIRCUIT PROTECTION IS
UL CLASS RK1 FUSE (AMP) : 20
SUPPLIED VOLTAGE : 600V, 3PH, 60HZ
I am confused as to the design for elevator load calculation to size generator. Because name plate, max accel ampere and fuse, all three number are different. Which ampere should I follow for load calculation?
Any knowledge on the subject will help or any reference as to where to learn more on this topic. Thank you!