Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Tek-Tips community for having the most helpful posts in the forums last week. Way to Go!

Emergency light

Status
Not open for further replies.

ramadanyoussef

Electrical
Sep 2, 2015
3
0
0
SA
if i have emergency light with built in backup battery and connected to a separate emergency circuit when i switch off how it recognize that it is switching case not power failure
 
Replies continue below

Recommended for you

Better check with the building, and other codes. It is normal practice to leave the emergency lighting circuits also on.
Hopes this helps
Dave
 
ramadanyoussef said:
in some areas it is connected to switches and in others connected directly to the panel

So they are using the light circuit for power supply and the switch box for junction? Most likely jumpered off the hot and not in series with switch. The only other type of switch I have seen on E-lights is a test switch located low enough to test the function of lights without needing a ladder.

Chuck
 
thanks for all i get the solution . it will be by adding one more wire from the switch to the lamp.
the lamp must be connected by four wires 2 line + neutral+ grounding
 
Status
Not open for further replies.
Back
Top