mechie101
Mechanical
- Sep 20, 2021
- 5
A customer has a central chilled water and steam plant that runs continuously year-round. Domestic hot water is created from the steam plant. The estimated hot water needed annually is 23,267 MMBTUs. The proposed measure is to install 4 water source heat pumps to heat the domestic hot water. The proposed equipment will create an additional 145 tons of chilled water while using the heat rejection loop to heat the hot water.
Baseline System
Chiller plant - 145 tons to be replaced annually. 0.75 kW/ton
Boiler Plant - 23.267 MMbtus to be replaced. 76% plant efficiency
Proposed System
4 WSHP - 145 tons total, 1.848 kW/Ton, condenser 2.656 mmbtu/hour
Will there be any energy savings for this customer, and if so, how much?
Baseline System
Chiller plant - 145 tons to be replaced annually. 0.75 kW/ton
Boiler Plant - 23.267 MMbtus to be replaced. 76% plant efficiency
Proposed System
4 WSHP - 145 tons total, 1.848 kW/Ton, condenser 2.656 mmbtu/hour
Will there be any energy savings for this customer, and if so, how much?