Epoxy Anchors at Cold Joint
spieng89
172
I have an existing spread footing I am adding on to and placing a pier above. Field observations have shown that, contrary to the original design drawings, the edge of the existing footing is inline with the epoxy anchor placement.
My question is, is it okay to proceed with epoxy install at this cold joint or would it be better practice to chip the existing foundation back a few inches and epoxy into the new footing expansion? The anchor rod location can not be moved due to project constraints. Attached a sketch
 http://files.engineering.com/getfile.aspx?folder=a80b032d-9ea2-42ec-93be-778ba2d32286&file=4668_001.pdf
What forces are you expecting in the anchor bolts?
Is this a gravity column? Part of a moment resisting frame? Part of a braced frame?
So what forces are you expecting in the anchor bolts?
Do you have a net uplift?
Horizontal shear parallel with the joint?
Horizontal shear perpendicular to the joint?
Gravity loads?
What are the rough magnitudes of the forces?
There will be net uplift occurring at this column of around 10 kips, but not sure why the magnitude of the uplift would be important if the anchors are designed for the intended load. My questions is whether the epoxy bond to the surrounding concrete would be affected being it's located at a joint.
Apply all factors related to cracked concrete for post installed anchors, that essentially what you have at a cold joint. As long as the joint is clean and has a concrete surface to bond to, it should work.....in theory.
I would be more concerned with how you provide flexural continuity in the footing itself. Why are you not just replacing it?
I suspect that the edge of the existing footing would not be properly cleaned and you would not get a good bond.
As an alternative:
I suspect that you could develop 10k of tensile force in the two anchors that do not fall on the joint.
I suspect that you could develop 10k of capacity in just the top "cap" and another 10k of capacity between the cap and the "lower" footings.