Epoxy in Masonry (High-Seismic Area) 1
JoMoEIT
8
I am working on a project out in California that requires us to use an epoxy system in fully grouted masonry cells. The Simpson catalog states
"When SET-XP adhesive is used with all threaded rod or rebar, the system can be used in tension and seismic zones where there is a risk of cracks occurring that pass through the anchor location. It is also suitable for uncracked concrete conditions."
The Test Criteria includes Post-Installed Adhesive Anchors in Masonry Elements (AC58); however, the building official rejected the epoxy stating it is used for concrete applications only.
Has anyone else had this problem (out of 50 projects in the SDC=D areas this is the first time it has been rejected)? What does everyone else spec for epoxy in masonry at a seismically active area?
What does the ICC ES report for the anchors state about masonry use?
Garth Dreger PE - AZ Phoenix area
As EOR's we should take the responsibility to design our structures to support the components we allow in our design per that industry standards.
I'm not surprised. If the ES report is for concrete, it can't be interpolated for CMU. I'd switch to an epoxy that has a CMU pedigree and ES report. There are some out there. It gets confusing, as we'd like to only have one epoxy on the project.
If I understand correctly, he OP said it was OK for masonry too: "The Test Criteria includes Post-Installed Adhesive Anchors in Masonry Elements (AC58)"
Perhaps you should call your local Simpson rep and engage their expertise.
Mike McCann
MMC Engineering
I called Simpson who directed me to an additional ER report (ER-265 for the curious). This report specifically states that the SET-XP epoxy can be used in fully grouted concrete masonry to resist earthquake loads. Further, the Simpson representative took it upon himself to speak directly with the city reviewer; wrapping up this problem quite tidily (Thank you, guys). One other question on a related note. Does masonry have a "cracked" designation like concrete design does? I haven't seen this mentioned anywhere, but it stands to reason that it would.