Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations GregLocock on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Equal distribution of air flow

Status
Not open for further replies.

168MVC

Mechanical
Jul 10, 2003
2
How do you ensure a 360 degree equal distribution to a tower shaped object when the input air supply is being fed through a square duct asymetrical to the tower from below?
Any help is appreciated.
 
Replies continue below

Recommended for you

Discharge to a plenum with 300 to 500 FPM velocity at the cross section and provide with perforations 360 degrees around duct. See United Sheet Metal perforated duct. The pressure drop through the perforations must be much greater than the pressure drop through the assymetric inlet to make the distribution equal. However you may have to use (4) register type diffusers, instead of perforated duct to get longer throw. You can then balance each with manual volume damper.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor