Equations for Strip Surcharge Loading Inconsistencies
swearingen
667
In all of the geotechnical and foundation books I have been able to round up post-1998, this formula (or one without the factor of 2) is given for the stress on a retaining wall due to a surcharge strip load. In books from 1998 and before, the pi in the denominator is replaced by H, the height of the wall. Obviously, the two equations give wildly different answers the deeper you go. To investigate, I compared a relatively narrow strip loading to a line loading formula and found that the pi aligns nicely.
What gives with this? Did Das find it was an error in '99 and change his books? It goes from H to pi in his books around that time. A Budhu book, "Soil Mechanics & Foundations" has the H in 2000, but others afterwards, including Pile Buck sources, have pi.
On similar note, a subject that has been touched on here before but not resolved to my liking - this formula seems to have a huge effect on short walls when applied at a good distance from the wall. Is this really the case? I put in a wall with a 200 psf surcharge (standard for us) but now they want to put a 20' wide crane pad 8'-2" away at 1300 psf. The wall is only 7'-9" toe to top. The lateral load went from 517 lb/ft to 3378 lb/ft. I expected it to be a good bit more, but it rising linearly with the load at a distance greater than the depth of the wall surprised me.
Any thoughts?
I have a request related to the formula - could you please take a quick look in your geotech/foundations text you have on hand, look up the lateral earth pressure due to a strip surcharge load formula, and provide whether it has the pi or H in the denominator? I'll start with what I've found so far:
H - Braja Das, Principles of Geotechnical Engineering 2nd Ed, 1990
H - Braja Das, Principles of Foundation Engineering 2nd Ed, 1990
H - Braja Das, Principles of Geotechnical Engineering 4th Ed, 1998
H - Muni Budhu, Soil Mechanics & Foundations, 2000
pi - Braja Das, Principles of Foundation Engineering 4th Ed, 1999
pi - Lindahl/Warrington, Sheet Pile Design by Pile Buck, c. 1998
pi - NAVFAC DM7.01, 1986
H gives wrong units. Pi gives correct units.
USACE EM-1110-2-2502 1999 uses pi.
US Steel sheet pile manual 1984 uses pi citing Teng 1962.
But Teng 1962 actually has different equation based on 2q/pi but with different sines and cosines. Not sure if can rearrange to match your/US Steel equation.
Check out Arcelor Mittal piling handbook for a different method. Free download. Pressure starts close to toe for your case. Should give result that isn't ridiculous.
You can compare these to Arcelor Mittal. Let us know if they all give similar answers or not.