Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations SSS148 on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Equipment wide pedestal: some doubts

Status
Not open for further replies.

Mainu

Structural
May 9, 2017
9
I have some doubts about the reinforcement of pedestals for the use of the industry equipment. A sketch is attached with concrete doubts,as example, about a chimney pedestal. If anyone know some good reference (book, code, ...) about this topic, I would be very grateful. Thanks in advance.

octagonal_y6xcqf.png
 
Replies continue below

Recommended for you


I'm not sure I've seen such a reference myself. It's just rules of thumb that get passed down in practice. In such a case (like you've got here) you would reinforce the perimeter (select a effective width, maybe 12-16") and reinforce it like a (stand-alone) wall. Between that "wall", is just considered fill. The re-bar you have going each way in the orthogonal direction (in the "fill") is a good idea too. (For crack control. Obviously, if this is some sort of environmental structure, you would need a detailed analysis for that.....and could no longer consider it "fill".)

Your perimeter would have to get as wide as necessary to insure that any anchor bolts fall into a reinforced zone. (Even if that means adding a "wall" in the interior to pick up any anchor bolts or support skids.)


 
Status
Not open for further replies.

Part and Inventory Search

Sponsor