SprinklerDesigner2
Mechanical
- Nov 30, 2006
- 1,251
This is the third ESFR I've been offered in the past two weeks.
An existing facility the owner asked if ESFR was possible and while I am sure it isn't I thought I would throw it up here.
Photo of concrete T roof deck.
We use the 2002 edition.
At the site, before I could review, I was thinking maybe the K25 if I could place the head in the center of panel maybe I could if I was able to keep the deflector 17 to 18" below the roof deck, as allowed by 8.12.4.1.2, and positioning in the center of the 4'-0" panel. The building less than 30' allowing 12' spacing to be used and we would be able to comply with Table 8.12.5.1.1 Positioning of Sprinklers to Avoid Obstructions to Discharge (ESFR Sprinkler)
8.12.4.1.2 Pendent sprinklers with a nominal K-factor of 25.2 shall be positioned so that deflectors are a maximum 18 in. (457 mm) and a minimum 6 in. (152 mm) below the ceiling.
But there is section 8.4.6.3* ESFR sprinklers shall be permitted for use in buildings with unobstructed or obstructed construction. Where depths of the solid structural members (beams, stem, etc.) exceed 12 in., ESFR sprinklers shall be installed in each channel formed by the solid structural members. Minimum sprinkler spacing and area of coverage shall comply with the requirements of 8.12.2 and 8.12.3.
The answer is so obvious but I have to ask anyway. It's impossible, right?
An existing facility the owner asked if ESFR was possible and while I am sure it isn't I thought I would throw it up here.
Photo of concrete T roof deck.
We use the 2002 edition.
At the site, before I could review, I was thinking maybe the K25 if I could place the head in the center of panel maybe I could if I was able to keep the deflector 17 to 18" below the roof deck, as allowed by 8.12.4.1.2, and positioning in the center of the 4'-0" panel. The building less than 30' allowing 12' spacing to be used and we would be able to comply with Table 8.12.5.1.1 Positioning of Sprinklers to Avoid Obstructions to Discharge (ESFR Sprinkler)
8.12.4.1.2 Pendent sprinklers with a nominal K-factor of 25.2 shall be positioned so that deflectors are a maximum 18 in. (457 mm) and a minimum 6 in. (152 mm) below the ceiling.
But there is section 8.4.6.3* ESFR sprinklers shall be permitted for use in buildings with unobstructed or obstructed construction. Where depths of the solid structural members (beams, stem, etc.) exceed 12 in., ESFR sprinklers shall be installed in each channel formed by the solid structural members. Minimum sprinkler spacing and area of coverage shall comply with the requirements of 8.12.2 and 8.12.3.
The answer is so obvious but I have to ask anyway. It's impossible, right?