ESFR

Status
Not open for further replies.

Randy S

Mechanical
Sep 3, 2024
2
0
0
US
8.12.5.3.2 Bottom Chords of Bar Joists or Open Trusses.
ESFR sprinklers shall be positioned a minimum of 1 ft
(300 mm) horizontally from the nearest edge to any bottom
chord of a bar joist or open truss.
8.12.5.3.2.1 The requirements of 8.12.5.3.2 shall not apply
where upright sprinklers are located over the bottom chords
of bar joists or open trusses that are 4 in. (100 mm) maximum
in width.
8.12.5.3.3* For pipes, conduits, or groups of pipes and con-duit to be considered individual, they must be separated fromthe closest adjacent pipe, conduit, cable tray, or similar ob-structions by a minimum of three times the width of the adja-cent pipe, conduit, cable tray, or similar obstruction.
 
Replies continue below

Recommended for you

What is your question here? Or are you just posting a section of the standard?

Travis Mack, SET, RME-G,
MEPCad, Inc
AutoSPRINK | AutoSPRINK FAB | AutoSPRINK RVT

 
Sorry - I was just responding to an inquiry about side by side obstructions less than 4'-0" in ESFR system. Was supposed to be linked to thread but didn't turn out that way...
 