Schmoleskin
Electrical
- May 10, 2007
- 7
How much effect does changing synchronous generator excitiation have on the mechanical load that the prime mover sees? Is it the same as KVA is to KW and KVAR, in the imaginary axis? I know that PSS uses this concept, but don't quite understand the relationship.
Have been working with a CAT technician who says they always set up their voltage regulators to operate in the 2 Volts/Hz mode to lessen the mechanical load on the prime mover while recovering from big load steps. I would like to hear if anyone disagrees with that philisophy.
Doesn't the V and 2V/Hz functionality make the generator look more like a big VFD while recovering from large load steps, lowering excitation to maintain proper V/Hz out to motor loads while frequency is depressed?
What are your thoughts on selecting V/Hz as opposed to 2 V/Hz? Does the type of load being served figure into this? For example, which would you want for primarily direct-connected motor load; or for load mostly served through VFDs?
Thanks, DJO