I'm looking at a project for expanding an existing 34.5kV Substation. Existing substation is a fenced in yard that has 34.5kV overhead feeders that transition to underground to feed 34.5kV Switchgear in prefab control building yard. The existing yard has 34.5kV - 4.16kV transformers with 4.16kV low side feeing switchgear lineup in same building.
Existing yard has crushed rock. Existing Substation grounding has a perimeter 4/0 ground around perimeter of yard and is tied to perimeter fence and is crisscrossed across yard to tie into specific equipment locations. I cant tell if grounding design was based on a ground grid study with step/touch cacls per IEEE or if grounding was based on some other "standardized approach"
Customer is not looking to expand the yard to put another control building which has switchgear fed from a parallel tap off of the same overhead 34.5kV utility lines. New switchgear will provide a redundant feed to existing transformers.
My question is with the expansion of the existing yard to install a new control house is it required to perform a ground grid calc and analysis per IEEE or would this fall under more of a "standard approach" with expanding existing yard grounding to just encompass the perimeter of the new control building to connect new building to existing substation grounding?
Existing yard has crushed rock. Existing Substation grounding has a perimeter 4/0 ground around perimeter of yard and is tied to perimeter fence and is crisscrossed across yard to tie into specific equipment locations. I cant tell if grounding design was based on a ground grid study with step/touch cacls per IEEE or if grounding was based on some other "standardized approach"
Customer is not looking to expand the yard to put another control building which has switchgear fed from a parallel tap off of the same overhead 34.5kV utility lines. New switchgear will provide a redundant feed to existing transformers.
My question is with the expansion of the existing yard to install a new control house is it required to perform a ground grid calc and analysis per IEEE or would this fall under more of a "standard approach" with expanding existing yard grounding to just encompass the perimeter of the new control building to connect new building to existing substation grounding?