I've designed a 75' simple span steel bridge with concrete deck.(Bridge is a private access bridge to a residence) Bridge is supported on grade beam and caissons. One end was detailed with base plate with slotted holes to allow for expansion. Contractor did not use slotted hole bearing plate. My concerns are:
1. Based on 40 degree temp. swing, axial load in steel stringer is about 420 kips. Modeled as a column considering P-delta, beam is no good.
2. Calculated length of expansion is only about .25". This seems minimal and yeilding at the support could accomodate the expansion.
Any thoughts or suggestions?