Thanks for valuable feed back, guys!
Jockey pumps are used in the system.
The piping system is extensive with fire ring mains serving hoses, hydrants, water canons, sprinklers, foam systems etc.
Elevation levels exceed 10 metres by far.
There are definitely air pockets in the system and air is probably also pushed in by the fire pumps as the air relief valves most likely can't release enough when the pumps start instantly.
100% air free priming of the system is not feasible. If the system actually hadn’t air pockets and vacuum was avoided (by starting the pumps before any water was released), then there wouldn’t be a problem like you are indicating Artisi.
Besides, air pockets may be good for cushioning pressure spikes.
I now know that it was a 10" riser that busted and that it happened at one of the higher elevations. An atmospheric tank was then installed to feed water into this riser as the water column drops in an attempt to avoid vacuum. When the large fire pumps starts then what I think happens is what Morten describes.
More than one phenomenon is probably occurring, pressure surges due to water-air-water flow and water hammer effects.
We will be making a simulation model. There is talk about a computer program called Pipenet. Just getting together enough information of what the whole system looks like is a big job. Morten, what simulation program have you used? And have your systems included a pressure tank for avoiding vapour pocket collapsing? And are your non return valves mounted further down in the riser than where the vacuum occurs preventing the water gushing back up the riser when the pumps start?